Post by emoncustomer on Jun 19, 2008 13:46:51 GMT -5
The load I wish to monitor has parallel feeds. How do I install the current sensors for this application?
|
|
|
Post by Suzy Abbott on Jun 19, 2008 14:28:48 GMT -5
There are two ways you can monitor parallel feeds. The first method is to clamp the sensors around all feed wires for each phase. The second method of monitoring parallel feeds is to clamp the sensor around one of the feed wires for each phase. When you read the meter, the final reading must be multiplied by the number of feed wires for each phase. NOTE: If you are monitoring multiple loads with one meter please view the "Multiple load monitoring instructions" thread. emondmon.proboards80.com/index.cgi?board=meterinstallationfaq&action=display&thread=33
|
|