Post by emoncustomer on Jun 19, 2008 13:48:34 GMT -5
I have 5 breakers in one panel I would like to monitor with one meter. Can this be done without paralleling current sensors?
|
|
|
Post by Suzy Abbott on Jun 19, 2008 14:23:52 GMT -5
Yes. Simply run all the breaker wires through one set of current sensors. Make sure all A-phase circuits are run through the A-phase sensor, and the same for B & C phases. The meter should be sized by the highest amount of current being monitored by one sensor.
|
|